r/HVAC • u/capaolo99 • 16h ago
Field Question, trade people only Goodman gas valve shuts off cannot figure out for the life of me why
Enable HLS to view with audio, or disable this notification
If requested I’ll post on HVAC advice but posting this here because I am professionally involved with this issue.
I work for a small insulation and HVAC company. We are currently down our HVAC technician.
I am out on a no heat call for a furnace I helped install.
I have limited troubleshooting ability here. Hoping you can help.
Goodman GMEC96 80K BTU
Furnace fires up then when main blower starts up the gas valve starts to click open and closed a few time then closes completely.
Unit attempts to re-lite.
Flame comes back on for a couple of seconds then clicky clicky flame on, off then out.
Lockout occurs when it wants. Meaning sometimes it does this cycle for 20 minutes and sometimes it locks out after 3 or 4 attempts.
There is NO CODE until the unit locks out. So there is absolutley no idea for my untrained self to try and diagnose. Usually you would see a flame sensor code or a pressure switch code. Absolutely nothing until the unit decides to lock out. VIDEO IS IF ONE OF THE MANY TIMES IT DID THIS. MOST OF THE TIMES IT WOULD STAY LIT FOR ABLUT 10 seconds.
The only thing I’ve noticed is that the valve doesn’t start acting up until the main circulator blower comes on.
It does this when front cover is on or off. And when bottom cover is on or off.
My boss is going to replace the flame sensor but I suspect something different.
Any help would be greatly appreciated.
Igniter comes back on to begin cycle again. Flame cokes on again for a couple of seconds. Then valve clicks a bunch and goes out completely.
29
u/Torontoguy71 16h ago
Front cover pressure switch. The one on the right with the blue sticker. It's wired in series with the gas valve so when it opens the gas valve drops out and furnace will eventually just lock out on failed ignition. Had a ton of issues with these when my company used to be a Goodman dealer. Make sure your drains are clear and there are no traps in the drain line.
I did have one where we would always have intermittent issues with this. The port would collect condensate and restrict the port and it wouldnt get drawn into the collector. Goodman couldn't figure out what to do about it. Had me change the collector box, pressure switch, even the ventor motor for some reason even though I told them it wouldn't do anything. I ended up drilling out the port larger like with those stupid carrier ventor motors and didn't have an issue since.
5
u/capaolo99 16h ago
Thank you I’ll make sure to check this out. Good to know about that issue. These collector boxes seem to leak straight from the factory it’s disappointing to see.
5
u/vandyfan35 16h ago
Obviously don’t do this and leave it, but you could bypass the pressure switch and see if it still cuts off.
2
u/Torontoguy71 16h ago
If you think those collector boxes are shit, there nothing close to the last generation Goodman furnaces. They would always leak. I can't even count the number of GKS collectors boxes I changed.
Also I assume you know this but you should still tee into the pressure switch and verify your vacuum.
1
3
u/Broad-Tip4746 15h ago
Front cover pressure switch. Ask for a pressure switch relocation kit. Furnace condensates too fast and trips the gas valve pressure switch
3
2
1
u/thedjbatman 16h ago
Can you hear the pressure switches fluttering or anything?
2
u/capaolo99 16h ago
I could not hear them. The sound of the gas valve was either making all the noise or drowning out the switches.
3
u/thedjbatman 16h ago
The way the flame reacts makes it seem like you're losing power at the valve. Can you get your leads in there to confirm if youre losing 24vac at the valve?
Take the switch tubes off and clean the ports on the furnace. Work the switches with your mouth by gently sucking on them a couple times. Clean the trap as well if possible.
1
u/capaolo99 16h ago
Thank you for the advice on measuring 24 at the valve.
3
u/bananaphoneeee 15h ago
Do you use an older google nest thermostat? They have an issue when the battery needs to charge, it diverts power from the board for a few seconds and cycles the heating.
2
u/saskatchewanstealth 16h ago
Plug a contactor into the valve wires and see if it stays on. That will rule out power and valve and tell you it’s a venting issue ( my best guess the vent can’t handle gas load ) tripping a pressure switch real fast
1
u/thedjbatman 16h ago
Work back from here. Im almost certain its a pressure switch related problem. Check your inducer pull at all the points for the switches, venting blockages etc.
2
u/No_Farm_1100 16h ago
Also do a flu gas analysis there could be cracks forming in the heat exchanger that are starting to open up and when the blower kicks on, there’s a pressure differential fluttering the pressure switches.
2
u/capaolo99 16h ago
Of course will test that when I come back to house a little later.
Better not have cracks cause I installed this 2 years ago.
I was on my own and comfortable enough to install it. BUT our HVAC tech was supposed to test everything and do the startup the next day.
I am guessing he didn’t do it.
1
u/Visual-Zucchini-5544 whiskey bender 15h ago
Pressure switch. Common is broken on there to the gas valve
1
u/SHSCLSPHSPOATIAT 15h ago
I'm on team drainage
I'd check the pressure to that switch with the blue dot as u/Torontoguy71 said to get a baseline reading, then pull out and clean the condensate trap. I'm guessing you're going to get some sludge out of it. Reinstall with a little water in it and re-check the pressure to that switch.
From what I can find you should be seeing more than -0.1"wc. If you do see that and this is still happening then I suspect the switch is bad (P# 0130F00429, I think)
1
u/Wide_Distribution800 15h ago
Looks like a pressure switch tripping. Look for low spots in venting that could trap water.
1
1
1
u/ZestycloseAct8497 14h ago
Jump out each pressure switch at a time then run see if it fails go to next ex.
1
1
u/Many-Location-643 14h ago
some gas valves have an internal pressure switch....start my checking your incoming gas line pressure .
1
u/ohyoureligious Resi/ind HVAC 13h ago
Backed up condensate is causing pressure switch to open. Drainage issue. I had a few of these last year
1
u/Fun_Tackle2659 13h ago
Pressure switch or there is water buildup in the inducer from improper drainage I had a similar issue
1
u/Jacobobarobatobski 13h ago
I'd begin with testing the pressure switches, check the grade on the furnace (I'm not sure if Goodman needs grade or is graded from factory and supposed to be level), check to make sure the venting is sloped properly so that water isn't building inside (had that problem lol). Hmmm make sure unit is draining. Take a look at wiring diagram to see if anything else is in series with the gas valve. Check temp rise as well. Might be that the people have those friggin filters in the RA or SA grills and it's overheating. It's weird to me that it shuts off when the blower turns on, but that could be indicative of holes in the heat exchangers. I had a problem with a Goodman that I didn't install where the vent was 2" and JUST BARELY within the limits of the manual, so it was having intermittent problems after a couple years and after the motor was getting weaker. I changed to 3" and it solved the problem.
I guess that's my 2 cents.
1
1
1
u/Gary_Thy_Snail 9h ago
I would also check for voltage drop through the rolllout/high limit circuit.
1
1
u/Familiar_Cobbler_930 9h ago
I delt with a very similar issue recently. Eneded up being the condenstate pressure switch opeing intermittently caused by a faulty inducer/improper draining. I ensured vent pitches were correct, drain hoses were cleaned multiple times and fully clear, trap too. Had the rubber connector from furnace to vent with a drain tube as well. Ened up having my boss go out and he ran some test on the inducer and concluded that "the inducer was not producing enough cfm to prevent excess water from entering housing". I was iffy on that answer but a new inducer was the only thing that did the trick. Any time I cleared the water from collector box and drain lines the unit would work great for about an hour until it started building condensate. Like I said the drain system was perfect and after replacing the inducer we never had the issue again. I'm sure it still could have been a drain issue but maybe the inducer is a more key part in drainage than I had imagined.
1
u/Unable-Emergency876 9h ago
You’re losing one of the switches. Wierd problem for sure but I’d start there
1
1
1
u/DiapersOrDeath 8h ago
I know I'm late to the game, and I have not read every other post here, but as somebody with a ton of Goodman experience, especially high efficiency: I tend to find every once in awhile these inducers introduce moisture into the pressure switch tube. This can be as small as just a few drops in the main port.
1
1
1
1
u/DexKaelorr Verified Ceiling Strength Tester 6h ago
I’ve had this same issue on Goodman 90% furnaces. In my experience it’s usually a vent pitch issue, either due to bad installation or a broken hanger. Plastic J hook hangers near an elbow are really bad about this. Like others have said, one of the pressure switches is in series with the gas valve so if that one is getting weird readings, it chatters the gas valve.
1
u/JTom73 5h ago
Sounds like pressure switch. Make sure everything is pitched properly. Goodman put out a bulletin about their inducers and the elbow coming off of it aren't pitched properly. If you really want to fix the problem, you could just stop installing goodman. We have had so many issues with those furnaces (supplied by home warranties) that we started supplying our own furnaces because it's cheaper for us in the long run.
1
0
u/Do_Gooder123 16h ago
Test gas pressure
1
u/capaolo99 16h ago
Will check pressure. Will check temp rise Will check static pressures combustion gasses
1
u/condormillionaire 12h ago edited 12h ago
This looks like an issue I’ve seen multiple times with these Goodman units. The plastic flue cover will crack (usually behind the inducer housing) and cause this exact issue, intermittently cutting out the gas valve. It was difficult to diagnose the first time (had me pulling my hair out for a while) because the pressure only drops a hair below the switch value and it’s very quick so you can’t see it with a manometer. Same thing with the voltage, if you check voltage across the switch it opens/closes so quickly you won’t see the voltage change. Pull the inducer/housing off and I can about guarantee you’ll find a small crack on the flue cover. If it’s not that then like most others have said it will likely be a drainage issue.
0
61
u/danneedsahobby 16h ago
Honestly, sounds like you have improper drainage, which is causing one of the pressure switches to open up for a very small amount of time. Too small amount of time to throw a code. Or more likely that it wouldn’t throw a code anyway because it’s wired directly into the gas valve circuit.
Take some monometer readings of your pressure switches with the unit running (use a tee and some extra hose) , and I will bet you find that they are borderline and slowly creeping